Hi all - hope to find some help here.
I want to integate a BOSCH 4 bar MAP and temp sensor to the PMU16 - should be an easy straight forward thing.
However, I dont get the temp sensor to read the correct value. I do use the wizard to give him the calibration of the BOSCH Temp sensor. But it will always read 250°C (while having 20°C) in the room because it keeps referring to voltage instead of resistance. I know the wizard tranfers resistance to voltage but keeps reading 0V whichis equal around 250°C - which is wrong.
Do I miss something here with pullup ?
Found issue - you have to set the 10k pullup twice. One in the main menu of the Input and one in the wizard...